Reply To: Problem with charging

#318755
BrokenDude
Participant

    Who done the electrical installation? From what I can see, EV aside, I don’t like that the tails are showing single insulation on entry to the Henley block which they should be double insulated until inside the block, and there is a CPC is not sleeved which is not compliant.

    When did you last have an EICR? I would heavily suggest getting one carried out soon because there, from what I can see, are some things that are easy to rectify but need done for safety.