Do you know what kW your shower is?
(1) 40A set aside as 100%
(2) Add the remainder together 32+32 +16+16+6+6 = 108
(3) 40% of 108 =(40×114/100) = 43.2
(4) 40+43.2 = 83.2kW current maximum demand
(2) 108+32 for charger =140
(3) 40% of 140 = (40×146/100) = 56
(4) 40+56 = 96kW new maximum demand with EV charger
Cut-out fuse upgrade to 100A BS7671
DNO calculation
Results
Total Estimated Maximum Demand Load per Customer 21.25 kVA
Total Amps 92.4 Maximum Demand
Total estimated maximum demand load 21.25 kVA
Total estimated load diversified for 1 customer(s) (This is the load we will use when we are designing the network)10 kVA
DN) may t0 downrate further on the day.