    Do you know what kW your shower is?

    (1) 40A set aside as 100%

    (2) Add the remainder together 32+32 +16+16+6+6  = 108

    (3) 40% of 108 =(40×114/100) = 43.2

    (4) 40+43.2 = 83.2kW current maximum demand

     

    (2) 108+32 for charger =140

    (3) 40% of 140 = (40×146/100) = 56

    (4) 40+56 = 96kW new maximum demand with EV charger

    Cut-out fuse upgrade to 100A BS7671

     

    DNO calculation

    Results
    Total Estimated Maximum Demand Load per Customer 21.25 kVA
    Total Amps 92.4 Maximum Demand
    Total estimated maximum demand load  21.25 kVA
    Total estimated load diversified for 1 customer(s) (This is the load we will use when we are designing the network)10 kVA

    DN) may t0 downrate further on the day.

     

     

     