Reply To: Ohme Charger Installation Process – Very Poor!

#237910
kezo
Participant

    @Glos Guy

    I going to pick daughter up in a bit. I’ll look more in depth when I get back 🙂

    You don’t have a smart meter by the looks of it?

    The service head (black box bottom left of 1st picture) has a 60A cutout, which would require a minor works order to uprate it to 80A or commonly 100A

    You would also require an 100A isolator installing

    It is “possible” to come of a consumer unit, providing there is enough spare wares and a double pole RCD is fitted, which you have. However it is better to take a supply and installing adedicated charger consumer  unit alongside or extenally. Though this depends on the existing tails fitted, and your whole home electrical demand.

    More later…